Flame Arrestor And Pv Valve (api 2000)

#1 User is offline   v8landy 

  • Veteran Member
  • PipPipPip
  • Group: Members
  • Posts: 31
  • Joined: 10-January 08
Reputation: 0
Neutral

Posted 01 September 2008 - 08:36 AM

Hi

As stated in API 2000 , 4.4.1.2

“a flame arrestor is not considered necessary for use in conjunction with a PV valve venting to atmosphere because flame speeds are less than vapour velocities across the seats of the PV valves”.

Then why do compnays sell combined PV valves and flame arrestors?

What is the chance of a flame (ignition source) being sucked into the PV valve of a tank?

I suspect more chance of a plane crashing into the tank!
0


Page 1 of 1
  • You cannot start a new topic
  • You cannot reply to this topic

Other Replies To This Topic

#2 User is offline   v8landy 

  • Veteran Member
  • PipPipPip
  • Group: Members
  • Posts: 31
  • Joined: 10-January 08
Reputation: 0
Neutral

Posted 05 September 2008 - 07:43 AM

Anyone???
0

#3 User is offline   v8landy 

  • Veteran Member
  • PipPipPip
  • Group: Members
  • Posts: 31
  • Joined: 10-January 08
Reputation: 0
Neutral

Posted 23 October 2008 - 01:09 PM

Anyone?
0

#4 User is offline   djack77494 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 1,157
  • Joined: 29-July 04
  • Gender:Male
  • Location:Anchorage, Alaska
Reputation: 8
Neutral

Posted 23 October 2008 - 01:30 PM

OK, OK. You've successfully solicited a comment, though of uncertain quality. I don't know about the relative speeds of escaping vapors vis-a-vis the flame front that is imagined as taking aim at the tank. I'm of a like mind in suspecting the plane crash scenario is more likely. I know combination flame arrestor/PVSV valves are made and marketed. One would assume they serve some purpose, and I can accept that they will perform as advertised (if in good condition). Personally, I've seen clients attempt to avoid them at all costs. They have small flow passages, and they can corrode or otherwise plug. If there is uncertainty concerning their ability to pass the rated flow when needed, then they are worse than nothing at all. If you buy and install them, I'd recommend good metallurgy for the elements and establish a program to test and maintain them.
0

#5 User is offline   v8landy 

  • Veteran Member
  • PipPipPip
  • Group: Members
  • Posts: 31
  • Joined: 10-January 08
Reputation: 0
Neutral

Posted 23 October 2008 - 02:56 PM

Thanks for the reply.

Now I have said that I will get to work tommotow to find a plane in the site!

I agree that they might have use but are more likley to cause problems if (when) they block leading to tank implosion via vacuum
0

#6 User is offline   Qalander (Chem) 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 709
  • Joined: 04-October 06
  • Gender:Male
  • Location:Karachi, Pk
Reputation: 6
Neutral

Posted 24 October 2008 - 01:39 AM

Dear v8landy Hello/Good Afternoon,

Although I would be not Competent enough to comment I believe. Still, its my way.

1) The comment about our Art. is below the decency level kindly abstain. Do keep/maintain noble human values in the forum please, request only.

2) I believe as experienced at my previous employers and contained in one of my previous replies; the flame arrestor& PVRV combination at times restricts flow both ways and may also play contributory role in over pressurization of tanks etc.

Best regards
Qalander
Earnest Regards
Qalander
0

Page 1 of 1
  • You cannot start a new topic
  • You cannot reply to this topic


Similar Topics Collapse

  Topic Forum Started By Stats Last Post Info
New Replies Icon Pilot Operate Safety Valve
BLOW DOWN ADJUSTMENT
Relief Devices Forum Arafat 
  • 1 Reply
  • 3,025 Views
New Replies Icon Waste Water And/or Energy Producing Equipment
feasibility studies
Student olrock 
  • 0 Replies
  • 145 Views
New Replies Icon Hysys, Tank Level And Pressure Control Question
dynamic state question
Chemical Process Simulation mavd25 
  • 5 Replies
  • 335 Views
New Replies Icon Sizing Minimum Flow Circulation Valves Industrial Professionals suresh786 
  • 2 Replies
  • 2,767 Views
*New Replies Icon Overpressuer Protection
how to design areliefe valve
Relief Devices Forum Guest_mohamed_* 
  • 1 Reply
  • 2,264 Views

1 User(s) are reading this topic
0 members, 1 guests, 0 anonymous users