What is the generelly acceptable range of velocity for tank filling line / inlet for say atmospherically vented Demineralised Water storage tank
0


Page 1 of 1
  • You cannot start a new topic
  • You cannot reply to this topic

Other Replies To This Topic

User is offline   fallah 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 982
  • Joined: 23-April 07
  • Gender:Male
  • Location:Iran
Reputation: 6
Neutral

Posted 20 October 2008 - 04:54 AM

QUOTE (ayan_dg @ Oct 20 2008, 03:30 AM) <{POST_SNAPBACK}>
What is the generelly acceptable range of velocity for tank filling line / inlet for say atmospherically vented Demineralised Water storage tank

I think,it is a nozzle sizing problem and the evaluation should be performed based on value of :density*velocity*velocity that normally when no inlet device is foreseen,should be Max. 1500 (in SI unit).Obviously,when inlet device is foreseen that value would be higher.
You can calculate the velocity as per above limitation.