Flutter Of Storage Tank Vents What is the "Flutter Zone"? #

User is offline   Steven McIntosh 

  • Newbie
  • Pip
  • Group: Members
  • Posts: 3
  • Joined: 11-May 09
Reputation: 0
Neutral

Posted 14 May 2009 - 01:20 PM

I'm looking for a definition of flutter as it relates to storage tank vents. My Protectoseal ® pro-flo II ™ software says that for certain combinations of flow, design pressure and set pressure all choices of vent style and size are in the "flutter zone". So, I'm looking for some info on just how bad is it to be in the "flutter zone". I've discovered one way out is to keep lowering the set pressure, but this isn't always desirable.
thanks,
Steven McIntosh
0


Page 1 of 1
  • You cannot start a new topic
  • You cannot reply to this topic

Other Replies To This Topic

User is offline   proinwv 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 217
  • Joined: 24-October 05
  • Gender:Male
  • Location:WV, USA
Reputation: 2
Neutral

Posted 14 May 2009 - 02:03 PM

Thanks Steve,

All of the common pallet loaded vents will flutter when operated close to the seat, or at very low flow rates as compared to the vent capacity. What happens is that the vent opens at the "setrpoint" and if oversized for the application or the actual flow to be vented, then it immediately vents and drops the pressure back to a reseat pressure. This is followed by a rise in pressure and the vent reopens, and the cycle repeats itself.

Using a smaller vent will avoid this, but there may be times when it will still happen.

The result is additional wear on the seat and stem or bearings due to the additional seating and wear cycles.

Paul

Paul Ostand
My Webpage
0

User is offline   Steven McIntosh 

  • Newbie
  • Pip
  • Group: Members
  • Posts: 3
  • Joined: 11-May 09
Reputation: 0
Neutral

Posted 14 May 2009 - 02:32 PM

Thank you Paul. I'm going to have to get back with you after a little more study. Everything you wrote makes perfectly good sense, but it's not exactly in-line with the results of the program from Protectoseal ®. (good program by the way) For example, without changing the size of the vent I simply had to lower the set pressure to get out of flutter. I suppose that could be considered to be taking the vent from over-sized down to proper sized.
I hope to have more to write by next Monday. In the mean-time, if you come across any "literature" definitions of flutter they might be helpful. I'm also wanting to learn more about inlet and exit dP and their impact on vents.
thanks again.
Steve
0

User is offline   djack77494 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 1,229
  • Joined: 29-July 04
  • Gender:Male
  • Location:Houston, Texas (formerly Anchorage, Alaska)
Reputation: 10
Good

Posted 14 May 2009 - 04:54 PM

Steve
You may find it easier to locate information on safety valve "chatter". I believe that the two (chatter and flutter) are very similar, though you must keep in mind that safety valves tend to "pop" while conservation vents (e.g. Protectoseal) are more like modulating valves.
0

User is offline   proinwv 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 217
  • Joined: 24-October 05
  • Gender:Male
  • Location:WV, USA
Reputation: 2
Neutral

Posted 14 May 2009 - 05:17 PM

Steven

Yes, by dropping the pressure, you require more vent to pass the same volume. I.e. less delta P more Cv required for the same Q.



Paul Ostand
My Webpage
0

User is offline   sheiko 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 265
  • Joined: 20-May 08
  • Gender:Male
  • Location:France
Reputation: 4
Neutral

Posted 27 March 2010 - 05:12 PM

View Postproinwv, on 14 May 2009 - 05:17 PM, said:

Steven
Yes, by dropping the pressure, you require more vent to pass the same volume. I.e. less delta P more Cv required for the same Q.


Sorry to interject myself in this discussion but i believe that by dropping the pressure (and thus the density), you require more vent to pass the same mass because the volume increase (mass= density*volume).

Please correct me if i am wrong.

Oupss...this thread is 1 year old...

This post has been edited by sheiko: 27 March 2010 - 05:21 PM

"We don't believe things because they are true, things are true because we believe them"
0

User is offline   fallah 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 982
  • Joined: 23-April 07
  • Gender:Male
  • Location:Iran
Reputation: 6
Neutral

Posted 28 March 2010 - 01:06 PM

The same volume (less mass) is correct, because the volume enclosed by liquid level and tank roof is almost fixed.

This post has been edited by fallah: 29 March 2010 - 12:30 AM

0

User is offline   fallah 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 982
  • Joined: 23-April 07
  • Gender:Male
  • Location:Iran
Reputation: 6
Neutral

Posted 29 March 2010 - 12:56 AM

View Postproinwv, on 14 May 2009 - 05:17 PM, said:

Steven

Yes, by dropping the pressure, you require more vent to pass the same volume. I.e. less delta P more Cv required for the same Q.


I think same Q wouldn't be achieved by the same size in less delta P.It could be achieved by larger size.
0

User is offline   Dazzler 

  • Member
  • PipPip
  • Group: Members
  • Posts: 22
  • Joined: 19-January 10
  • Gender:Male
  • Location:Australia
Reputation: 1
Neutral

Posted 04 April 2010 - 07:11 PM

An alternative way to move away from flutter or chatter zone for vent valves (tank vents or vessel pressure relief) would be to have say two valves (or multiple valves), one smaller at a lower set pressure and then a second valve set at a slightly higher pressure. Smaller flow scenarios are therefore likely to only open the first valve and it would stay open longer rather than fluctuate as a larger single valve may be expected to.

I believe this is why it is important for relief valves to have all relief scenarios identified (for flowrate), incase there is a frequently expected scenario of smaller flow that needs to be considered specifically so that a single valve does not chatter.

Dazzler
0

User is offline   fallah 

  • ChE Jedi
  • PipPipPipPipPip
  • Group: Members
  • Posts: 982
  • Joined: 23-April 07
  • Gender:Male
  • Location:Iran
Reputation: 6
Neutral

Posted 05 April 2010 - 01:08 AM

View PostDazzler, on 04 April 2010 - 07:11 PM, said:

An alternative way to move away from flutter or chatter zone for vent valves (tank vents or vessel pressure relief) would be to have say two valves (or multiple valves), one smaller at a lower set pressure and then a second valve set at a slightly higher pressure. Smaller flow scenarios are therefore likely to only open the first valve and it would stay open longer rather than fluctuate as a larger single valve may be expected to.

I believe this is why it is important for relief valves to have all relief scenarios identified (for flowrate), incase there is a frequently expected scenario of smaller flow that needs to be considered specifically so that a single valve does not chatter.

Dazzler


Just to add my comment on above nice statements:

Most PSVs to be designated such that can tolerate smaller flow than rated flowrate which those PSVs sized based on,in order to cover different scenarios without chattering.The limitation in most cases would be 25% of rated flowrate.

This post has been edited by fallah: 05 April 2010 - 01:31 AM

0

Page 1 of 1
  • You cannot start a new topic
  • You cannot reply to this topic


  Topic Forum Started By Stats Last Post Info
New Replies Attachments Continous Opearted Valve
what is this
Refining, Hydrocarbons, Oil, and Gas dgoyal 
  • 1 Reply
  • 1,708 Views
New Replies Hysys Math Error
what does "math error" mean in HYSYS
Chemical Process Simulation chemtan 
  • 4 Replies
  • 4,869 Views
New Replies Heat Exchanger
Factors determining what to be put into the shell and what into tube
Student conan_kaya 
  • 2 Replies
  • 489 Views
New Replies Tank Liquid Entrainment Relief Devices Forum thabom 
  • 0 Replies
  • 469 Views
New Replies Thermowell Leak
what provisions are required to find leak in thermowells
Industrial Professionals adivaraghan 
  • 4 Replies
  • 1,007 Views

1 User(s) are reading this topic
0 members, 1 guests, 0 anonymous users