A plant expansion has been designed considering 150# steam, and the setting of the steam safety valves in the expansion is at 150#.
Steam for this expansion will be supplied from the existing steam system, that operates normally at 200 psi but has a design pressure of 250 psi.
I am planning to install a pressure reducing valve on the supply line to the expansion, and a safety valve downstream this valve, with a capacity that matches the flow through the pressure reducing valve 100% open (valve failure case) and at maximum upstream pressure. Is this an adequate arrangement and design criteria?
I also have some specific questions:
1. Should I take into account the relieving pressure of the boiler safety valve (250 +10%) to determine the capacity required for the new safety valve? I don't think so because it would be a case of double jeopardy, but will like to hear opinions.
2. Any suggestion of a specific kind of control valves to use in this application?
Any additional input would be appreciated.
Thank you
|
|
Relief Device For Steam System Expansion
Started by Luigi, Apr 17 2007 11:23 AM
2 replies to this topic
Share this topic:
#1
Posted 17 April 2007 - 11:23 AM
#2
Posted 18 April 2007 - 05:35 AM
QUOTE
A plant expansion has been designed considering 150# steam, and the setting of the steam safety valves in the expansion is at 150#.
Steam for this expansion will be supplied from the existing steam system, that operates normally at 200 psi but has a design pressure of 250 psi.
I am planning to install a pressure reducing valve on the supply line to the expansion, and a safety valve downstream this valve, with a capacity that matches the flow through the pressure reducing valve 100% open (valve failure case) and at maximum upstream pressure. Is this an adequate arrangement and design criteria?
Steam for this expansion will be supplied from the existing steam system, that operates normally at 200 psi but has a design pressure of 250 psi.
I am planning to install a pressure reducing valve on the supply line to the expansion, and a safety valve downstream this valve, with a capacity that matches the flow through the pressure reducing valve 100% open (valve failure case) and at maximum upstream pressure. Is this an adequate arrangement and design criteria?
I would think your arrangement is OK.
Note : Your 150# rating test pressure (125%) may be higher than the CV maximum upstream pressure. If your downstream equipment (design to ASME) are protected from CV failure case, you may have a chance not to provide PSV on the piping...please check the piping code if short term pressure excursion upto test pressure is allowed...
QUOTE
I also have some specific questions:
1. Should I take into account the relieving pressure of the boiler safety valve (250 +10%) to determine the capacity required for the new safety valve? I don't think so because it would be a case of double jeopardy, but will like to hear opinions.
1. Should I take into account the relieving pressure of the boiler safety valve (250 +10%) to determine the capacity required for the new safety valve? I don't think so because it would be a case of double jeopardy, but will like to hear opinions.
I would think it is double jeopardy as normally boiler has it Hi-Hi pressure and temperature trip.
QUOTE
2. Any suggestion of a specific kind of control valves to use in this application?
With such low pressure drop CV, normal control valve good for high temperature service (valve seat & extended stem) is good. Noise level should be lower than 85 dBa as low dP...Just have to conform with CV vendor.
Good steam engineerig tutorial link... http://www.spiraxsar...g-tutorials.asp
JoeWong
#3
Posted 18 April 2007 - 01:08 PM
Thank you for your comments.
Similar Topics
Thermal Relief Valve For A Fire CaseStarted by Guest_QuantumEng_* , 19 Nov 2025 |
|
|
||
Sizing Fire Case Relief Valve Installed Below Liquid LevelStarted by Guest_processrock_* , 14 Apr 2026 |
|
|
||
Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
|
||
Ethylene Plant - Is The Dilution Steam Generation System An "unfirStarted by Guest_Alfreedo_* , 12 Mar 2026 |
|
|
||
Steam Condensate HammeringStarted by Guest_sandeepk2022_* , 06 Mar 2026 |
|
|

FB