Thank you Art for your excellent explanation and I also recall an instance where the Hexane blanketing valves were relocated to the tank top. I could not understand the significance that time.
The blanketing nitrogen header pressure is at 3 bar and the tank height is 5 metres.
The blanketing valve is self actuated PCV and is set at 300mmWC(30mbar).
Now if the pipe is full of Heptane:
P =H* rho*g 5*770*9.81=0.3bar(300mbar).
Or will the PCV sense this Hydrostatic head downstream the PCV and never open..
Due to the wide swing of temperatures from day to night the HC will vaporise and not retain its liquid phase.
The liquid draw off is only 2m³ per day.So this may be one of the reasons why the valve is still at grade.anyway I will speak to my bosses.
Finally, Art I respect your engineering knowledge,expertise and experience.As an operator the knowledge I have gained from you through this forum is immense.