I am working on becoming our corporate expert on Pressure Relief. I've read all the ASME & API standards.
We have a consultant who is recommending fusible plugs for tank jackets in a fire case to drain the liquid out of the jacket prior to it reaching its boiling point because the existing valves aren't sized for 2 phase flow.
I have several concerns about fusible plugs while I admit the valves are probably not large enough for 2 phase flow. They were sized for all vapor flow, which was the industry standard.
- Plugs aren't in the ASME Pressure Vessel Code
- You have to locate the plugs near the bottom of the vessel so if you have a fire in one room you could drain the cooling water for the entire building on to the floor of that room.
- Plugs have an unknown maintenance requirement. One website recommends replacing them every year. That would mean draining all of the cooling water system to do the replacements.
- Plugs can become corroded on the inside or outside and fail to operate.
I've talked to the manufacturer of the fusible plugs and they said Bayer and Dow use fusible plugs for this type of service.
What does anyone else think? Any experience with fusible plugs?