QUOTE (Art Montemayor @ Oct 18 2007, 06:58 AM)

Linus:
First of all, refer to my earlier comment on your other thread. Emergency Vents are just that; they are meant for emergencies – not for normal operating vent requirements. What you have described seems more like the conventional Conservation Vent – a device that is meant to relieve both for pressure and vacuum conditions and, in my experience, never used for emergency venting. Therefore, if that is the case then you have to respect the need for vacuum protection and relief.
I’ve done the application that you describe many, many times. We called the installation a vent “control” – why, I don’t know; it never “controlled” anything. It merely scrubbed the vapors positively vented from a storage tank, prior to the same vapors being vented to atmosphere.
The design I employed used a Conservation Vent (CV) to meter out the vented vapor going to the scrubber. I’ve used 2” and up to 4” sizes for this application. I agree with Phil; I also suspect the original designer/installer didn’t know what he/she was doing - especially if there is no documentation on the installation. The reason I employed a CV was that I maintained a positive pressure (an N2 blanket) on the stored liquid product and didn’t allow venting until a top set pressure was exceeded. If you are not blanketing, then there is no need for a CV. Now, there may be a reason for installing a CV: suppose there is a possibility of the scrubber getting plugged (we don’t know the fluids used or the chemistry). If that were a possibility, then the need for a CV is obvious – but not vented to the same scrubber!
Depending on your process and application you may need the vacuum relief. Perhaps that is the use that the CV is being put in for. It could be that there was no simple vacuum device available at the time and someone decided to put in the CV for that purpose – ignorance is everywhere. When a production plant or facility does not maintain detailed and accurate calculation and data files and documentation on their engineering installations that is what happens – and often! Don’t let that happen to you.
Unlike JEBradley, I can’t suggest any specific line size. We don’t know the vapor capacities, the tank size, the fluids, the application, etc.. You have to do the calculations – even if they are estimates. You can always estimate conservatively – and document the calculations and assumptions.
Thank you Art Montemayor, as usually your knowledge and experience make us understand the problems easily.
But related to this topic I have another question: Suppouse the case of an
atmospheric vessel with a normal operation vent discharching to a vent collector where more vents discharche, and then going to a vent condenser. Then in case of an emergency (for example fire) the pipe vent size must be much bigger than the normal operation vent, and I wonder if the vent header wich goes to the condenser must be designed for emergency case, and thus the vents condenser ¿??? In that case the condenser will be over-dimensionated.
¿Is it a right solution to dimensionate the vent header and vent condenser for normal operation and place a PSV in the vent header covering all vessels the discharge there? In that case all the vessels will be pressurized in case one of them is in emergency.
Can you help me with this, please??
Thank you again