I have a separator, It is having ESD valve on feed intlet, vapor outlet, liquid outlet lines. These ESD valves are initiated by LIZA (1oo2)-high high (During LIZA trip feed inlet ESD valve closes, Liquid outlet ESD open, vapor outlet ESD closes) . Now there is a LCV on liquid outlet line which is controlled by an independent Level transmitter.
My first question whether I need to size the relief valve for liquid blocked outlet.??
My assumption is During LICA malfunction, vessel is having independent LIZA(1oo2) which will close the feed inlet ESD and will stop the feed, hence liquid blocked outlet case is not a valid scenario. Plus the time required for reaching the level from High High trip to vessel top is more than 30 mts so this scenario is not valid.
My second question is whether I have to consider the malfunction of IPF, say during high high level is the LIZA(1oo2) initiates the ESD valve, it fails to close. And the level in the separator rises which will pressurize the vessel and the liquid relief occurs through the relief valve. Is it a valid scenario. Whether we need to consider the failure of IPF.
Regards
Umesh