Dear all,
I'm facing in my office an internal discussion relevant to LS steam header protection, downstream a split range controlled let down station (2 x 100 t/h let-down with desuperheater, both in service but normally closed).
Let's suppose to have a HS header connected to a LS header through let down system made by 2 x 100 t/h pressure control valves (with desuperheater) controlled in split range from LS pressure.
Designing LS steam header PSV I have to suppose that both valves are driven open because the failure of controller ore one is enough???
Consider that LS header has also one vent 100 t/h capacity.
If the LS pressure controller would have high integrity level (e.g. 2oo3 Pressure transmitter) this would be enough?
Regards
Rob