QUOTE
What's the service of the 3-phase separator ? Is it Slugacatcher or inlet separator or first separator receiving offshore fluid from pipeline ?
I do not know exact service of the sparator but it is the first one receiving fluids from other platform.
I also calculated the size of PSV for relief in case of external fire but got only 1 sq in. I get close to 11 sq in only if I consider 2 phase relief through the PSV. Does it mean that this case would give me the required flow rate?
QUOTE
Is there analysis done on number of vessel exposing to fire simultaneously within a fire zone ? Have you considered those PSVs within a fire zone lifting during fire case ?
I do not know if such analysis was done but I will look into it. Good you have mentioned multiple PSVs relief during fire!
QUOTE
If this PSV is a standard, pop open type valve (Farris 2600 series for example) then the tail pipe is sized for the PSV rated (stamped) flow. I can't be more clear than this.
It is exactly Farris 2600! By the way, thank you for explaining how to recalculate rated flow in one of previous topics.
QUOTE
Simultanious relief should always be considered for your flare, as mentioned earlier fire is one, but one can also think of total cooling water failure, total power failure or total instrument air failure.
Is there a list of scenarios that one should look at or you learn it during years of experience?
Thank you all for comments and advices!!!