Hi all-
I have 2 questions on a PSV application; please hlep me in answering the questions.
Thanks a lot.
Regards
srin
Application: PSV on steam drum
Background:
2 PSVs are provided on steam drum (from waste heat boiler) and the steam drum is constructed as per ASME Section VIII. Design pressure of the steam drum is 39.3 bar g and the maximum steam generation rate is 21000 kg/hr @ operating pressure (35.5 bar g). I need to calculate relief load (blocked exit scenario) for these PSVs and also I have to ensure that the PSV inlet nozzle size is adequate (the PSV inlet nozzle size has been fixed by process licensor as 2" each).
Set pressure of PSV 1 is 39.3 bar g
Set pressure of PSV 2 is 40.4 bar g (1.03*39.3)
Relief load basis:
I am planning to share the total steam generation rate between the two PSVs equally; so, PSV relief load would be 21000/2 = 10500 kg/hr each.
Query:
1. Is it acceptable to use 6% accumulation for PSV1 & 3% accumulation for PSV2? By doing this, I am able to get the size 2J3 which matches with the 2" PSV inlet nozzle; also, pressure drop across the PSV inlet piping is below 3% of PSV set pressure. ASME Section I says that total accumulation should not exceed 6% of MAWP and with the above proposal, the code requirement is also not violated.
2. For calculating PSV orifice size & rated flowrate, I am using 10500 kg/hr as required relief rate; I have been told by my senior that 10500 kg/hr is the mass flowrate at normal operating pressure (35.5 bar g) and so I should not use it; instead I may need to use the mass flowrate at relieving pressure (41.7 bar g). If that is the case, how do I need to calculate the mass flowrate at relieving pressure? My thinking is as per mass conservation theory and so the steam massflow rategenerated will be the same irrespective of pressure (whether 35.5 or 41.7 bar g). Please clarify my queries.