I am analyzing the relief system for some propane horizontal vessels, and found they are using multiport manifold with 3 or 4 relief valves (similar to REGO's).
In one of them, the inlet connection to the manifold is 4" and each of the 4 individual relief valve has a 2 1/2" inlet. Even considering that only three of them will relieve simultaneously (the 4th is closed by the manifold), the inlet area to the manifold is less that the total area of the relieving valves.
Questions:
1) Is this situation acceptable under good engineering practice? API 521 says that the first consideration to design inlet piping is to provide full inlet area as a minimum, however, it looks that is only a recommendation. Being these valves in the market, makes me believe that this could be acceptable.
2) Some of the valves are rated under UL and not ASME: Is is right that ASME code requires valves rated unde ASME only or there are exceptions that allows the use of valves rated under UL?
3) If the valves where rated at 20% accumulation, is it allowed to recalculate their capacity at 21% (fire case) or they have to be "re-rated" under ASME by the manufacturer?
4) Anybody has experience calculating the pressure drop in the multiport manifolds? It looks that manufacturers don't have information available.
Any comment will be appreciated.