Dear All,
Here is the situation.
(1) 3rd Party Nitrogen line to Site Plant with Max. Operating pressure 18 barg.
(2) At Battery limit, A PCV control the site header pressure @ 9 barg.
(3) Downstream of the PCV, a PSV protected the site nitrogen header with set pressure @ 12 barg. Relief to Atm. Sizing scenario is the PCV fails. Preliminary sizing result in a 4P6 Pilot valve with modulating action. Pop-up open PSV not selected due to concerns of big impact on site downstream plants.
(4) The Site header line size is 4".
(5) PSV inlet line ( consider 5 feet, one ball valve ) preliminary sizing result in 6" line, . Inlet loss 0.3% of the set pressure.
when i put the exlarger 6"x4" (Nitrogen header to PSV inlet line.) and reducer 6"x4" ( PSV inlet line to PSV inlet nozzle) in the final inlet line calculation, found the exlarger/reducer significantly increase the pressure drop and result in inlet loss 4.1% of the set pressure. I use the Crane book A-26 and Page 2-10,11 to calculate the Enlarger and Reducer K value ( based on 6" line).
question is.
a. whether Crane calculated K value can be used for vapor?
b. Any idea how to deal with this situation?
Thanks in advance,
nli2