QUOTE (joshofindia @ Mar 11 2008, 05:37 PM)

I am trying to estimate new PSV for old drum. Basically we are using old drum in our plant, relocating it to new location and using it with totally different service.
New PSV inlet size matches with old drum PSV nozzle, but inlet and outlet piping pressure drop is coming 5.70% and 16.51% respectively.
I am using safety factor of 1 to calculate del. P /100 ft. I want to know what is standard safety factor is used in industry.
Do we at all need to apply safety factor for PSV inlet and outlet piping pressure drop?
As far as i know we apply safety factor to cover pressure drop due to unknown pipe design (one more elbow or lil. extra pipe in piping design state). But in my case i made sure that pipe designers are using exact joints and pipe length that i used for piping pressure drop.
Your input on this will be highly appriciated.
Thanks,
amit Joshi
We don't know if your service needs to comply to API STD 521 for your company's SAFETY policy. We also don't know what type of PSV e.g. conventional type, etc and what is blowdown for selected PSV.
If API STD 521 shall be complied, one of the requirement in this standard is the pop action pilot operated and conventional spring loaded type PSV inlet and outlet shall be sized based on rated flow whilst modulating type pilot-operated may consider required flow.
You mentioned that "...inlet and outlet piping pressure drop is coming 5.70% and 16.51% respectively.". Can you please detail the 5.7% and 16.51% ? Does it refer to 5.7% of set pressure, relieving pressure or others parameter ? What type of PSV ?
Personally i do not worry much on the safety factor used but i worry your system experiencing chattering and under capacity PSV...
If you provides required informations, may be we can provides some useful advice.