I have the next doubt. I am checking a engineering and I found the next specification for a Relief Valve :
Type: Conventional Bonnet not vented to Atmosphere.
Set: 10 Kg/cm2g
Flow: 1 MMSMCD natural gas (PM 19)
When I checked the Built Pressure of the vent piping system i get the next result:
Constant Pressure: Atmosphere
Built Pressure: 1.7 Kg/Cm2g
The total back pressure is clearly more than 10% of set pressure that is usually recommended for Conventional Relief Valve. So…
From Reference 1 (see below) only the set of the valve will be affected but not the Capacity. But what will be the real set point? Could the valve chatter?
On the other hand from reference 2 I read that the capacity could be affected to? That´s correct? Which one is right?
Thanks in advance.
Ariel
Reference [1] Surface Production Operation Volume 2 Page 369 – Ken Arnold & Maurice Steward-.
Reference [2] – GPSA Engineering Data Book – Figure 5.10