QUOTE
I have written in detail about drum and feed oils in reply to Mr. Dong. Please take reference from there.
1) As per your opinion, I should consider 25 ft height but I have to subtract 10 ft height of elevation and in that case, 25 ft-10ft=15 ft height should be considered for wetted area calculation which is more than normal liquid level but less than HHLL. Is that o.k OR irrespective to drum elevation, should I consider 24 ft TL-TL height for wetted area calculation? OR Should I consider 15ft height with bottom piping of around 10 ft length to calculate wetted area?
I am getting confuse with the provided information at different posts.
Simple sketch tell all stories. Can you please kindly roughly draw and upload for evaluation ?
QUOTE
2) Another view is that generally double jeopardy is not being considered. I mean HHLL and external fire both happen together should be considered as double jeopardy or not.
System will not trip prior to HHLL. HHLL (just before touching) can be reached before a fire is started. Two scenario are exclusive and sequential between each and other. So, they are not double jeopardy.
QUOTE
3) I am using HYSYS. Dear Joe, things are not clear but I followed you as below.
3.1) I feed the pressure upto Set point +21% in the stream of blend composition of all three oils. As operating temperature was sub cool so I put VF=0 and corresponding temp came 306 degF. At this time heat flow was 819 btu/hr.
3.2) Increased temperature to 308 degF, VF came .0004 & Heat flow = 817 btu/hr. Not much change and no flow in vapor phase.
3.3) Actually what do you mean by "partially release vapor from vessel until the volume is same as initial volume". I tried to bring VF=0.01, at this VF, temp came out 434 degF and heat flow is 739 btu/hr and mass flow in vapor is 0.2 lb/hr. Now If I subtract 817-739=78 and latent heat = 78/0.2=390 btu/lb, looks very high.
3.4) I increased VF to 0.1 then temp=604 degF, Vapor mass flow=6.2 lb/hr, heat flow=615 btu/hr. In this way, Latent heat = (817-615)/6.2=32 btu/lb which looks low. At VF=0.2, LH= (817-585)/14.3=16 btu/lb.
3.5) At VF=.027, vapour flow=1 lb, temp.=527, heat flow=675 btu/hr so LH=(817-675)/1=142 btu/lb.
I don't know what should be the right approach?
4) How to decide relieving temperature & mol wt. in this case?
5) How can we reach upto Set pr.+21% pressure in Hysys by adjusting VF & temperature as we don't know temperature & VF at relieving condition and to get this pressure, number of combinations of temp. & VF are possible.
In my opinion, the initial system definition at 3.1 is not representing the real system.
(i-1) Define fluid in the vessel is at maximum Operating pressure (P0) & operating temperature (T0) and maximum liquid level (L0) prior to fire start. The system volume (V0) will be defined by the physical vessel dimension and piping volume. The system volume (V0) can be vapor volume (Vv0) and liquid volume (Vl0)
(i-2) Adjust the inventory (vapor mass and liquid mass) in the vessel until you achieve the vapor volume (Vv0) and liquid volume (Vl0).
(ii) Input some heat into the system to bring the the system upto relieving pressure (Pr0=121% of Pset). By maintaining system volume at V0. At this point, your system is at relieving condition. The temperature at this point is Tr0.
(iii) Next step is further input heat (Q1) to achieve 1-2 deg C above Tr1 but maintain pressure at Pr0. Normally the total volume at this point potentially higher than V0. If yes, proceed to (iv). if not, further increase the temperature (Tr1) until the liquid start to flash but maintian pressure at Pr0.
(iv) Remove part of the vapor (m1) from the system to bring the system volume back to V0.
(v) the latent heat is approximate with Q1/m1. If you found the LH change significantly, change the 1-2 degC according.
(vi) Calculate the time (t1) required base on Q1 and fire load calc from API equation.
(vii) Calculate the PSV size base on m1, t1 and other properties.
(vi) Repeat (iii) - (vii) until you get the maximum PSV area.