My first reply - hope it works.
The BDV remains open throughout the depressurisation - API 521 is quite clear on that, I believe. Normally (in my experience), BDV's are supplied and configured in the control system (high integrity shutdown system) such that they are "manual reset". This means that the activating solenoid has a physial pushbutton that must be pressed to re-close the valve. Such a reset should only be possible once the cause of the ESD/blowdown has been rectified and cleared through the shutdown system. If the cause is not "cleared" then pressing the button won't close the solenoid valve and the BDV itself. Consult your Control systems/instrument engineer.
Another point is that blowdown should only really be initiated on a confirmed fire (some offshore facilities also do so on confirmed gas leak as well), in which case, operating philosophy should be to allow the blowdown to continue to "zero" or steady state flare header pressure hich should be very low in a shutdown case. I have operated offshore and if designed properly, it doesn't take that long to completely blowdown. Your simulation should show this.
Hope this helps.
QUOTE (fallah @ Sep 19 2008, 06:27 AM)

Dear all
Can someone say what should the BDV status be, after depressurizing - from operational point of view? I mean, after reaching the isolated vessel pressure of 50% of design pressure or 100 psi (based on API 521) BDV should be closed or would be opened. That in the latter case, the mentioned vessel pressure will be equalized with the flare system pressure and we need purging for next start-up.
Regards