Re-Rating / Replacing Tanks...
Started by styx, Dec 13 2011 04:49 PM
2 replies to this topic
Share this topic:
#1
Posted 13 December 2011 - 04:49 PM
""
#2
Posted 14 December 2011 - 03:23 AM
styx,
What is the tank operating pressure? Is the tank equipped with blanketing system?
Seems due to higher vapor pressure of isopentane you need to consider higher operating pressure, hence you should evaluate new operating pressure besides tank design pressure.
Anyway, please submit the above information for better assistance.
Fallah
What is the tank operating pressure? Is the tank equipped with blanketing system?
Seems due to higher vapor pressure of isopentane you need to consider higher operating pressure, hence you should evaluate new operating pressure besides tank design pressure.
Anyway, please submit the above information for better assistance.
Fallah
#3
Posted 14 December 2011 - 08:54 AM
Styx:
This is an excellent, practical engineering topic.
I’ve had storage tank re-rating projects and I would consider this assignment as an important one with a high priority due to the relative large tank size. My immediate response to your basic questions is:
1) Normally, a tank re-rating is very possible and feasible. I would certainly consider this option first;
2) A replacement with a spherical tank is a major and very expensive decision and one that I would reserve as a last resort. I personally don’t think a spherical design is justified for this application and size.
What I recommend – and what I would undertake (if it were my project) is the following:
You fail to state what you consider as “ambient” temperature or what country (or region) your tank is in, so it is impossible to second guess what would be your yearly average tank vapor pressure. However, as the workbook indicates, the Isopentane is lighter than Hexane and, as such, the physical loadings and stresses on the tank would be lessened by the application – as compared to design.
Please note that you failed to state the basis for your tank’s design pressure – whether gauge or absolute. I have had to assume that you meant gauge pressure, because that is the normal engineering fabrication custom. You may have to change out the PSVs on the tank to suit the Isopentane operating conditions.
I hope this helps you.
This is an excellent, practical engineering topic.
I’ve had storage tank re-rating projects and I would consider this assignment as an important one with a high priority due to the relative large tank size. My immediate response to your basic questions is:
1) Normally, a tank re-rating is very possible and feasible. I would certainly consider this option first;
2) A replacement with a spherical tank is a major and very expensive decision and one that I would reserve as a last resort. I personally don’t think a spherical design is justified for this application and size.
What I recommend – and what I would undertake (if it were my project) is the following:
- Obtain a copy of API 653, “Tank Inspection, Repair, Alteration, and Reconstruction” and thoroughly study it in detail;
- Obtain ALL the engineering design and calculations regarding the fabrication of the subject tank – this should include nozzle loadings, Maximum Allowable Working Pressure (MAWP), Maximum Allowable Working Vacuum (MAWV), Pressure Relief Devices, etc.;
- Obtain the services of a recognized and experienced engineering firm that can carry out a thorough tank inspection and generate a formal engineering report on the subject tank’s condition and integrity, once inspected, - complete with recommendations as to the proposed future application.
You fail to state what you consider as “ambient” temperature or what country (or region) your tank is in, so it is impossible to second guess what would be your yearly average tank vapor pressure. However, as the workbook indicates, the Isopentane is lighter than Hexane and, as such, the physical loadings and stresses on the tank would be lessened by the application – as compared to design.
Please note that you failed to state the basis for your tank’s design pressure – whether gauge or absolute. I have had to assume that you meant gauge pressure, because that is the normal engineering fabrication custom. You may have to change out the PSVs on the tank to suit the Isopentane operating conditions.
I hope this helps you.
Attached Files
Similar Topics
Sil Rating Requirement For BurnersStarted by Guest_seuenergy_* , 13 Apr 2024 |
|
|
||
Determination Of The Number Of Foam Chambers For Storage TanksStarted by Guest_AnbIran_* , 15 Feb 2024 |
|
|
||
Rating Of Existing Condensate Fractionator With New Heavy CondensateStarted by Guest_adnanaslam1988_* , 03 Feb 2024 |
|
|
||
Overpressure Protection For TanksStarted by Guest_Chemcato_* , 21 Dec 2023 |
|
|
||
Cuestions About Storage TanksStarted by Guest_Quimarah_* , 01 Oct 2023 |
|
|