Psv Fire Case - Design Temperature

10

This topic has been archived. This means that you cannot reply to this topic.
2 replies to this topic
Share this topic:
| More

#1 mm217

mm217

    Veteran Member

  • Members
  • 49 posts

Posted 21 December 2011 - 03:08 AM

Dear all,

I will be so thankful if anybody could help me to deside:

I'm designing a case:

Fire case PSV
Fluid: water;
Set Pressure= Design Pressure= 7.5 barg;
Design Temperature= 85 C
Relief temperature is calculated= 181 C < 593 C (carbon steel) , so PSV is applicable.

Should i change the vessel design temperature from 85 to 181?!!!

#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,026 posts

Posted 21 December 2011 - 03:42 AM

Dear all,

I will be so thankful if anybody could help me to deside:

I'm designing a case:

Fire case PSV
Fluid: water;
Set Pressure= Design Pressure= 7.5 barg;
Design Temperature= 85 C
Relief temperature is calculated= 181 C < 593 C (carbon steel) , so PSV is applicable.

Should i change the vessel design temperature from 85 to 181?!!!


mm217,

Not at all. Fire case shouldn't be the basis of the vessel's mechanical design.

Fallah

#3 mm217

mm217

    Veteran Member

  • Members
  • 49 posts

Posted 21 December 2011 - 04:03 AM


Dear all,

I will be so thankful if anybody could help me to deside:

I'm designing a case:

Fire case PSV
Fluid: water;
Set Pressure= Design Pressure= 7.5 barg;
Design Temperature= 85 C
Relief temperature is calculated= 181 C < 593 C (carbon steel) , so PSV is applicable.

Should i change the vessel design temperature from 85 to 181?!!!


mm217,

Not at all. Fire case shouldn't be the basis of the vessel's mechanical design.

Fallah


Fallah;

Thank you very much.