in gas turbine performance book , i found this equation for air enthalpy calculation
H=a(T-T0)+b(T^2-T0^2)/2-c(1/T-1/T0)
the constants a,b,c and the mass fraction of air constituents are provided
T0=273k
T=288k
i did apply in the equation as in the attached sheet
by sum the last column i got this value for enthalpy, the book says the enthalpy is 14.876 kj/kg
any idea
thanks in advance
Edited by slmn, 09 April 2012 - 02:18 PM.
#2 kkala
kkala
  • Banned
  • PipPipPipPipPip
  • 1,939 posts
Posted 13 April 2012 - 06:40 AM
Heat capacity of air is roughly 0.24 kcal/kg, so you need 0.24*4.19*15 ~ 15 kJ to heat 1 kg air from 0 to 15 oC, which is in rather good agreement to 14.876 kJ/kg of the book.
Attached "Rev0.xls" contains the spreadsheet of enthalpy calculation, with some remarks on it. No arithmetic errors could be traced, it seems that the application of enthalpy formula for gases contains some error. Probably the units? Resulting heat capacities for gases are not realistic, as indicated in the added columns.
Check formula for enthalpy again, error cannot be specifically located by me. Hopefully tracing will be easy.
Editing note: Added "1 kg" on Apr 15th, 2012
Edited by kkala, 15 April 2012 - 05:48 AM.
#3 ankur2061
ankur2061
  • Forum Moderator
  • 1,995 posts
Posted 13 April 2012 - 11:03 PM
slmn,
What you are looking for is psychrometric calculations for wet or humid air including the entahlpy of wet / humid air.
In such a case refer the excel spreadsheet, "Psyschro.xls" attached in the link below:
http://www.cheresour...6833#entry26833
#4 slmn
slmn
  • 6 posts
Posted 13 April 2012 - 11:17 PM
thank you fot the great help