Hi All,
From the fuel gas system HYSYS model I developed, I noticed that the HC dew point of the gas @ stream condition is 62.22 deg.F. The stream condition are temperature @62.23 deg.F and pressure @ 250 psig. The fluid is a fuel gas to be supplied to a GTG.
1) Would this close HC dew point temperature to stream temperature affect the property of the fuel gas to the GTG?
2) Should I consider the installation of a heater to increase the flow temperature when the FG condition required by the GTG is within the range of 45.8 - 48 deg.F and 242 - 250 psig?</p>
Hc Dew Point Temperature Vs Stream Temperature Of Fuel Gas
Started by asade abiodun, Aug 29 2012 03:20 AM
1 reply to this topic
Share this topic:
#1
Posted 29 August 2012 - 03:20 AM
#2
Posted 16 October 2012 - 07:19 PM
Hi Asade,
you need to see the lowest temperature in the plant area,
at the stream conditions (62.23 degF; 250 psig) there is no problem, but there will be liquid formation at the lower temperature caused by environment.
installing heater or heat trace the line is common for fuel gas supply to the users (boiler, etc)
Regards,
RoyenG
you need to see the lowest temperature in the plant area,
at the stream conditions (62.23 degF; 250 psig) there is no problem, but there will be liquid formation at the lower temperature caused by environment.
installing heater or heat trace the line is common for fuel gas supply to the users (boiler, etc)
Regards,
RoyenG
Similar Topics
Max.service TemperatureStarted by Guest_kasri_* , 22 May 2013 |
|
|
||
Refinery Fuel Gas And Fuel Oil PriceStarted by Guest_ajsc_* , 13 May 2013 |
|
|
||
Filter Coalescer On Teg Column Outlet Stream (Gas)Started by Guest_Ali-Jabbaran_* , 11 May 2013 |
|
|
||
Blowdown TemperatureStarted by Guest_shan_* , 07 May 2013 |
|
|
||
Lean Amine Split Stream Filter CartridgesStarted by Guest_josh68_* , 08 May 2013 |
|
|


FB