Thank you very much Dacs for your reply, you will find my answer and comments for each of your question in blue color.
Before I answer to your interrogations I want to bring additional details about the water, in fact the water I’m talking about is not a seawater but a water coming from our natural gas well after being separated its like a brine; the composition of this water is close to seawater.
Where did you get this 45 psiA value?If it goes to an open source, then you have to use atmospheric pressure. In general, it's the process requirement that sets the endpoint pressure, not the other way around.
There is no process requirement what we just want to use 2 applications for the water stored in water tank coming from our natural gas well after separation. In one hand we want to evacuate water to the sea via PVC pipeline length 5,000 m and the other hand we want to use this water (from tanks) during civil works of future well site platform located at 5 km, we will use this water for watering the ground before the construction of the well site pad.
So I guess following your answer since it goes to an open source I only need atmospheric pressure 14.67 psi if ok for you I will apply this value.
Another thing, how did you obtain the 132 gpm flowrate? I think you need to fix this first before doing your hydraulics. As a guidance, you can set your flow based on some hold-up time that your process needs. How much? That's something you need to evaluate but it could be as low as 2 mins or as high as 30 minutes. Ultimately, it's going to be dictated by your process needs.
How did I obtain 132 gpm flowrate? We have 3 tanks with a capacity of 30 m3 each, so we want to empty each tank in 1 hr so 30m3/hr/tank in gallon that’s give 132 gpm flow rate
We normally expect that suction line size is larger than discharge line size due to NPSHa requirements (so check your basis for sizing both lines). For the suction, you'd normally place a strainer (which has a pressure loss requirement). That's something you need to add. It's seawater so I think it'll be way below its boiling point (so NPSHa may not be of much issue).
The current suction line is 3 inch because it was install like this couple years ago I were not there and the discharge line we want to use is 3 inches could this choice work by considering NPSHa requirements, I re-attached the excel file showing all fittings, valve with their quantity cause I don’t have a program to run isometrics.
Unless you precisely know how you'll route your piping (such as having the pipe isometrics), you have to use some design factor in estimating your pipe lengths. And to add, the number of fittings for your discharge seems low for its length (~5 km).
I know precisely the pipeline route but I don’t have a program to do isometrics I have only excel program to do my design but I attached you a Google earth pipeline route with elevation profile for your information.
Thank you very much for your advices.
im waiting back your reply.