This is what I gather from your screenshot.
It would appear you have an ammonia plant with a reformer for making hydrogen and an ASU for generating nitrogen for this purpose.
HIC1004 is some input parameter to control FIC1002 N2 Compressor Discharge flow to a certain amount wrt to the hydrogen flow? and in this case it is at 75.7% open and 23.08barg.
PIC1650RS is actually the remote setpoint calculated by the Performance Controller. The pressure PV is taken from PI1631.
The Performance Controller controls the compressor by controlling the IGV which is currently at 22.7% (23% is the commanded value from the controller), and by controlling the recycle valve FV1602 which is currently at -0.2% (0.0% is the commanded value from the controller).
Evidently your setup is one where capacity control is by a combination of IGV and recycle control whereby both discharge flow and pressure are controlled by the controller
When suction pressure is increased, the discharge pressure and flow will also increase. Since the recycle is already fully closed, the IGV is then closed to reduce the flow and pressure back to the setpoint.
I too feel the dp across PIC1623 might be a little too high. PIS1623A/B/C are all showing low pressure alarm. Perhaps the discussion would benefit from knowing the design pressures for the compressor inlet and outlet as well as the flow and more info on this valve, otherwise it could be hard to make an informed judgement.
Is it possible to modify the setpoint for PIC1650RS? There is still some leeway on FIC1002 as it is only 75.7% open, assuming this screenshot is of the plant running at full load. In fact, the discharge pressure PI1002 appears to already be giving a high pressure alarm (HI)!!! If you reduce the discharge pressure setpoint, FIC1002 will open more to achieve the required flow and overall you will definitely get some improvement.