I have another documentation question. Per sub-note ( b ) on Table 9 in API 2000 (6th edition), the F factors are calculated based on the following equation in API 521:
F = (InsCond * (Tmax - Tfluid))/ (66570 * InsThk)
One discrepancy is that API 521's F factor equation uses 66570 W/m2 instead of 66200 W/m2 which is mentioned in subnote b.
Another issue is that I cannot match the calculated F factor values using either constant. For example (for the first row)
F = (22.7 W/m²K * 887.9 K)/ (66570 * 0.025 m) = 12.11
How, then, was the value 0.3 in the table calculated?
I thought maybe 887.9 K was not the temperature differential as stated in note ( b ), but the relieving temperature:
F = ( 22.7 W/m²K * 16.1) / (66570 * 0.025 m) = .022
Close but no cigar.
Neither of the methodologies work if I use 66200 W/m²K, either.
Can someone help me validate the calculated F factors?