Dear All,
As per API 2000.to calculate normal venting there to method Using latitude and all on pg.6 of API 2000 6th Edition.
Method-1
Incase of Thermal Out breating
Say for tank Cpacity 30000 m3,Non-Insulated,lattitude < 42 ,(Factor=0.32).
i get value of 3424 Nm3/hr.
Method-2
But buy using another direct method given in Annexure A,with Flash point<37 nad B.P <149 Deg C.
i get value of 2495 Nm3/hr.
Why so difference, is it beacuse Method -2 considered B.P and flash point or something else.?
Also Which will correct answer?
Another Case
Also i want to calculate same for 90000 m3 tank?
Method-2 can't be used or i have to explorate the same.
Also it say for calculation of Capacity more then 30000 m3 refer to body of Internation Standard.
So shall i use Method-1 ?
Pls Help.
Regards,
NK