Dear ziba,
Nothing attached as edited EXCEL drawing...
Seems the tank has been blanketed with natural gas, am i right?
Anyway, an additional protection layer to protect the tank against overflow in the case of LIC failure can be: considering a level switch triggers the ESDV to be closed and at the same time the pumps to be tripped in HH position...
Hope above helps you out...
Hi:
I forgot to attach the edited file,Sorry here you are.
Yes tank is blanketed and produced gases are connected to VRU suction manifold.
So my undersatnding is that " you mean that having the valve is not necessary? and it is redundant" but what about ABSA rules for PROTECTION OF LOW MOP side of system ,
I have attached a sheet from ABSA for pipeline pressure control and over-pressure protection, high pressure pipeline is connected to the water tank , pipeline design pressure = 300 ANSI rating , it is connected to an atmospheric tank with design pressure of only 3.45 Kpag.
pipeline is designed based on CSA and the inlet header from pipeline designed based on ASME.
Based on ABSA regulations ,all sources of over-pressure including operator error and those involving fire , start up and shutdowns and upset scenarios should be accounted (including instrumentation malfunctions.)
Please let me know if there are other options than" level switches on tank to close inlet ESDV"?
How can I improve the control with added valve . There are two files attached, appreciate if you take a look at ABSA file, many thanks again
Thanks