On plant I have an issue with a rather large valve. Due to a sudden process disturbance (blast furnace slip), the pressure in front of this butterfly valve suddenly increased. In the event of a slip, the valve should immediately fully open. However in this case the valve closed against its mechanical stop resulting in a pressure excursion. Downstream pressure remained constant.
There are two theories; poor maintenance of the actuator or under sizing of the actuator (I am also looking at incorrectly sized valve). I have given the manufacture a call who should be able to give me actuator sizing charts but I wanted to check some first principles.
To size the actuator I did the following.
Required actuator torque = dynamic torque due to fluid forces + bearing torque + seating torque.
Item 2 I have from the valve specification. Item 3 is 0 here as the valve cannot fully close. Thus I need to calculate the dynamic torque.
Dynamic force (N) = upstream (dynamic + static) pressure (N/m2) * area of valve (m2)
Thus I can get a torque rating for different openings and different pressure events. I can do this by multiplying the above force by the height of the valve.
The question; should I be using differential pressure instead of upstream pressure for my calculation?
Any other comments are appreciated.