I am increasing Chemical dosing only if Steam TDS is high , not if Bfw quality is low , I was just wondering whether TSP removes hardness as well as Silica , or is silica removed by IBD , also since CBD removes sludge which floats on water it cannot be the same thing which is removed from the bottom of the reboiler since it is lighter that water and IBD material is heavier ..
If BFW quality is low, and your CBD is low, then the boiler water will be high in TDS and silica content. The TDS and silica in the steam increase with those in the boiler water, it is as simple as that, so if the steam TDS and/or silica are too high, your CBD is probably too low. There may be too much boiler water entraiment (carrying solids) in the steam drum, but there is not much you can do about that, except lowering the water level in the drum (but keep it above the CBD drawoff). Foaming may also cause water carryover into the steam. Foaming can be caused by organics in the BFW due to poor operation of the condensate polishing unit.
Dosing trisodium phosphate (TSP) will reduce dissolved Ca2+ and Mg2+, but I think it affects dissolved silica only slightly by its impact on the water pH, moreover it does not reduce the anions (sulphate et cetera) originally associated with the Ca2+ and Mg2+. It merely replaces dissolved Ca2+ and Mg2+ by dissolved Na+ so the TDS in the boiler water is not affected much. The precipitated calcium phosphate and any precipitated magnesium salts (phosphate, hydroxide, silicate) are to be removed every now and then by opening the IBD.