Hi Everyone.
A level control valve is placed at inlet of a low pressure storage tank (N2 blanketed to positive pressure). Inlet liquid is coming from a different unit within plant from a pump discharge. This pump is supplying sub cooled liquid to various users.
This tank is provided with a PCV located at vent line.
Pressure at inlet to level control valve is 3.2 barg. If level control valve fails open (control valve failure) high pressure liquid around 3.0 barg would hit bottom of low pressure storage tank.
My understanding is in this case, tank PCV would not protect the tank. Tank may fail due to high inlet liquid pressure as hydrotest pressure would be exceeded. So, inlet pressure should be lowered at inlet of level control valve or the supply should be from a dedicated pump (pump should be sole supplier).
Please advice your opinion.
Regards.