Dear all,
Thanks for your great efforts that encourage me to ask the following question;
Based on API RP 512, blowdown valve is required when the operating pressure is 1700 kPa or higher. Also, the blowdown system should depressurize the system down to 690 kPa or half of the design pressure within 15 minutes. Here comes the question, one of our engineers suggested to have a PSV (designed based on fire case) that sets at the half of the design pressure of a horizontal separator knowing that the operating pressure of that separator is lower than 690 kPa. She says that she is following the standard however, I am not comfortable with that solution.
What do you think about this solution as she claims that the PSV will replace the blowdown valve and as a result the blowdown valve will not be purchased.
I know that PSV does not protect the system from fire case and the solution during fire emergency is to depressurize the system (manually for example) using blowdown valve.
Thanks in advance