Presently i am facing problem in deciding set point values of hot well levels in surface condenser in a power plant.We are having surface condenser with five levels; High High,High,Normal,Low & Low Low.
1) Generally we try to maintain hot well level at 0 MM or normal level.
2) If hot well level falls below 0 mm, normal make up valve will open and allow DM water to condenser in order to maintain normal level.At Low level this normal make up valve will be fully opened.
3) If hot well level goes below Low Level, emergency make up valve will open to bring back the liquid level in normal level.At low low level Condensate extraction pump will trip.At this Normal Makeup Valve & Emergency Make up valve will be in fully open condition.
4) Similarly at high level a dumping valve will open and allow excess water from condenser to be dumped in Condensate Storage Tank and try to bring back the hot well level in normal value.
5) At high high level the steam inlet to condenser will be closed to avoid overflow.
Can anybody please tell me how can i decide the high High,High,Low , & Low Low level set point. Is there any guideline for this?