Lokesh,
It appears that, before submitting your post, you didn't read the explanation in the link i attached to my previous post; because you did repeat almost what is included in the mentioned explanation...
Kryz,
Yes, the set point of a PSV can be higher than the MAWP of the relevant vessel. Read the second post of the discussions included in the link of the attached file....
Kryz,
Yes, the set point of a PSV can be higher than the MAWP of the relevant vessel. Read the second post of the discussions included in the link of the attached file....
Dear All,
Thanks to all of you who replied to my post. Finally after investigation, I found that the PSV I am talking about are suplemental.
It was proposed initially the PSV-XXX set pressure to be 11,377 kPag (same as MAWP). However, original designer raised the concern regarding interaction this PSV with other PSV’s in plant, particularly with PSV-YYY for 4th stage discharge compressor relief. This particular PSV-YYY is set also 11,377 kPag and it is sized for blocked outlet of compressor discharge scenario. It is undesirable to have PSV-XXX on TEG contactor to pop up during blocked outlet scenario, as PSV-YYY serve for this purpose. It will cause relief valve to chatter as some load could be taken by fire relief PSV on TEG contactor. That statement was documented in the original design basis, and decision was made to elevate set pressure of PSV-XXX to 110% of MAWP, which is 12,514 kPag.
The concern raised by original designer in opinion of author of this post is too conservative. It can be demonstrated that PSV-YYY for compressor blocked outlet is located closer to compressor discharge than Contactor fire relief PSV-XXX. When overpressure scenario (blocked outlet) will occur the pressure gradient (pressure losses) between PSV-XXX inlet and PSV-YYY inlet will prevent second valve to pop up (if both would be set at 11,377 kPag). When already first PSV is relieving, actual pressure at second PSV will be always lower than its set pressure (due to flow frictional losses). Hence it is possible to bring back set pressure of PSV-XXX to originally proposed 11,377 kPag.
I am thinking of recommending that our client do this eventually. (Change set pressure back to 11,377 kPg)
However, as this PSV is sized properly, any alteration/interruption might not be desired by plant operation unless it is safety related problem. The PSV setting complies with the design code (ASME, API), hence this is not a safety issue. Moreover, consideration is required for other relief valves in the plant - i.e., like for TEG coalescer and Lube Oil Coalescing Filter where the PSVs also need to be reset to the same pressure as TEG Contactor (all those three PSV are fire relief cases with small D orifice size and set @ 12514 pig), as inconsistency in set pressure may affect when each valve pop-up during relief scenario, as described in the beginning of this section. The purpose of selecting set pressure is to ensure the relief valve will open for scenario which PSV is determined, fire PSV and block outlet PSV are different in the plant, and they must only open for those contingencies which they are designed.
So this is my concern to prevent me to do this recommendation. (Change set pressure back to 11,377 kPg)