Dears:
What is your idea about safety shutdown valve by pass
Before and after shutdown valve need to be equalized with small diameter pipe or not ?Do know any standard for this matter.
Thanks in advance
M.R.Rahimzadeh
|
Posted 18 November 2014 - 06:14 AM
Dears:
What is your idea about safety shutdown valve by pass
Before and after shutdown valve need to be equalized with small diameter pipe or not ?Do know any standard for this matter.
Thanks in advance
M.R.Rahimzadeh
Posted 18 November 2014 - 06:38 AM
Mr. Rahimzadeh,
In general a SDV is authorized, in safety standpoint, having an equalization by pass line; a ESDV is not....
Posted 19 November 2014 - 03:34 PM
Why would you not want an equalization line?
I am no expert in this area but am generally interested. My understanding is that the equalization would reduce the opening torque meaning a smaller actuator which means the valve could be cheaper. And of course the opening / closing times would be more rapid.
So would you not have equalization in a SSDV and ESDV alike?
Posted 19 November 2014 - 04:24 PM
ESDVs can not be bypassed from the safety point of view. if a equalization line is needed, this line should have another ESDV installed or lock closed block valve.
Edited by hianbotech, 26 November 2014 - 01:32 PM.
Can Anyone Provide Me The Reference Datasheet For Deluge Valve?Started by Guest_Radha Krishnan Siva Kumar_* , 16 Apr 2024 |
|
|
||
Valve Cv InputsStarted by Guest_QuantumEng_* , 01 Apr 2024 |
|
|
||
Pressure Control Valve Issues For Gsw LinesStarted by Guest_fahadazh_* , 29 Mar 2024 |
|
|
||
Self Actuated Pressure Reducing ValveStarted by Guest_panagiotis_* , 16 Feb 2024 |
|
|
||
Kvs Value Control ValveStarted by Guest_panagiotis_* , 05 Feb 2024 |
|
|