What happens if I use a control valve one size higher than the line size? I know we always use a line size control valve or one size less than the pipe line. Since I have a situation where vendor can not give 1/2" valve but offered 1" valve, where as the line size is 1/2". Checked line sizing and 1/2" line is perfectly O.K.
Can anybody clarify?
No problem. I do recommend to check the line sizing. Basically, if the line size is correct (within the suggested velocity limit), the control valve should be smaller or equal to pipe size. Quite rare to see the control valve bigger than line size. 2ndly, try some other vendor. I have an experience that some vendor cannot provide control valve ¼” but flowserve can provide it. Other thing is, the smaller, the cheaper. That’s why always go for the smaller control valve.