Currently there is an argument for the minimum flow line for transfer pump (centrifugal pump). Related info is as per below:
- The transfer is from a mobile tanker to an atm storage tank.
- Transfer time is about 2 hours and will be guide by operation.
- Pump flowrate: 10 m3/h
- Discharge pressure: 5-6 barg.
Argument:
- For pump protection, I do proposed to have relief valve at discharge, set at shut off pressure or less than that. PSV discharge will be at pump curb and open drain before goes to treatment (since the PSV flow is small [should be 5m3/h or less] and service is not critical and toxic). Basically, the reason to consider relief valve is because if I do consider minimum flow line, I have to route back to the suction which is not good practice. Plus, I need to resize the pump, motor, piping and etc. since minimum flow line using orifice. And by using relief valve, it still can protect the pump in case of shut off condition.
- Consultant said, centrifugal pump highly preferred to consider minimum flow line for pump protection. It will be rout back to pump suction and should be ok. PSV is not recommended and normally use with PD type pump.
Question:
- Is it PSV valid for pump protection in case of block discharge or shut off pressure?
- What is another impact (other than undistributed heat in the system) if we have minimum flow line that goes to the suction?
- Which one is the best method?
thank you