Good day.

I the sour water plant, we have a sour water tank. This tank has an injection of fuel gas to avoid an explosive environment into the tank. The tanks also has an Vacuum Breaker Valve to avoid the deformation of the tank structure in case the injection of fuel gas fail. The Vacuum Breaker Valve is at present to the atmosphere, and i think if the Vacuum Breaker valve is activated in an event of low pressures in the tank, the income of air it´s going to make an explosive environment into the tank, therefore the question is, do i should conect the vacuum breaker valve to another blanketing gas? for example Nitrogen. Have you seen cases like i´m relating?

Greetings!

#2 pleckner

pleckner

    Gold Member

  • ChE Plus Subscriber
  • 564 posts

Posted 26 April 2006 - 07:33 PM

We typically don't design for failure cases, we design to protect against failure. That is the purpose of the independent backup vacuum breaker valve, designing to protect against failure of the primary vacuum relief. Saying this, it is not uncommon to do as you are suggesting. Just make sure that the backup system is highly reliable. I would set up a frequent preventive maintenance program to ensure the integrity of the backup system as this would be the last line of defense against a catastrophic tank failure.

#3 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 27 April 2006 - 02:32 PM

Cesar,

I agree that we need to design to avoid the problem.

Let me ask you a question. If you blanket with N2 rather than fuel gas, and there is a vacuum valve actuation, would it be less likely to reach a dangerous atmosphere, being that you are starting both O2 and fuel free?

Also, a properly designed and maintained blanketing system should provide proper pressure control to eliminate the opening of a vacuum vent valve.

One method that might interest you would be to use a cascade blanketing system in which you had two blanketing valves with set points somewhat displaced from one another. For instance, one set to 1 in.wc and the second set to -(minus) 1/2 in.wc. The vacuum vent would be set to say -2 in.wc.The valves would open whenever the tank pressure was below their setpoint, so under normal operating the higher set point valve would operate, and should it fail the negative pressure valve would come on to keep the vacuum at or above a certain level. Should it also fail, then the atmospheric vacuum vent opens and an alarm system can be employed to warn of this and shut down any pump off operation.

The pressures are for example only. Actual values depend on the tank MAWP and MAWV.

Please exercise design care should you use such a system and be in contact with suppliers to understand the operanting curves of the hardware.

Best wishes
PAUL

#4 César

César

    Brand New Member

  • Members
  • 4 posts

Posted 02 June 2006 - 12:24 PM

Thank you all for your coments!

I agree that the most important thing in this case is ensure a reliable system to provide the blanket gas.

Paul, you are right, it would be better to blanket with N2, taking in account that it´s a non explosive gas, however, this decision implies the instalation of a new system of blanketing.

I like the alarm system idea.

My decision it was the following:

I think that for a vacuum pressure in the tank, it should matter two things at the same time, 1) Fail in the blanketing system 2) Decrease in the level of the tank. The probability of this two events at the same time is very small. What i´m going to do is to put an alarm system when the pressure in the tank is 0 psig.

Thanks you all for your contribution!
Best regards!!!

César

#5 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 02 June 2006 - 04:30 PM

Cesar,

There is another situation where the failure can occur; sudden cooling of the tank, caused by a rainstorm.

The probability of a multiple failure is finite.

The penalty for a failure could be loss of the vessel due to vacuum collapse, damage to other property, loss or contamination of product, injury or death. It is difficult to justify such a decision after an accident.

Further, should the tank pressure be dropping and your alarm sounds, then what do you do? Run?

I wish you luck.

PAUL

#6 César

César

    Brand New Member

  • Members
  • 4 posts

Posted 16 June 2006 - 12:39 PM

Good day Paul.

>
QUOTE (proinwv @ Jun 2 2006, 05:30 PM) <{POST_SNAPBACK}>
>Cesar,

>There is another situation where the failure can occur; sudden cooling of the tank, caused by a rainstorm.

In this case the blanket system will provide more gas to increse the pressure.

>The probability of a multiple failure is finite.

Yes, you´re right

>The penalty for a failure could be loss of the vessel due to vacuum collapse, damage to other property, loss >or contamination of product, injury or death. It is difficult to justify such a decision after an accident.

Exactly, and the vacuum breaker valve is going to be put to avoid a vacuum collapse. Remember that what i don´t want is to let the atmospheric air comes into the tank through the Vacuum Breaker Valve, because this situation it would generate an explosive atmosphere.

>Further, should the tank pressure be dropping and your alarm sounds, then what do you do? Run?

The alarm will alert the operator that the pressure is coming down and he will take actions to avoid the pressure fall below the set of the vacuum breaker valve. One action he can take is, for example, decrease the outlet flow of the tank. If the operator can´t avoid the pressure fall below the set of the vacuum breaker valve this valve will let air enter in the tank, after that the operator will stop the plant until the blanket system can be repaired.

>I wish you luck.

Thank!!

>PAUL
>


Best Regards.
César

#7 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 16 June 2006 - 12:47 PM

Cesar,

I understand what you are saying, and the sequence.

However, my concerns are that you relying on a human response, and even a judgement, and relying on this response being timely.

I simply do not believe that this is a safe way to proceed. Possibly some others who are monitoring this thread will jump in and give us their advice.

PAUL

#8 Guest_Guest_*

Guest_Guest_*
  • guestGuests

Posted 22 June 2006 - 02:30 PM

blanket with nitrogen is basically my first and only recommendation.

but at least look at how much the tank normally breathes and what type of overall mixture you would have in the tank. is it possible to have an optimum explosive mixture or is the oxygen coming in going to be so little during the typical level changes and potential breathing, can you get to a flammable mix?

but even with that said, you will not have perfect mixing in the tank and you will have 100% air at one point at the inlet and you will have 100% gas at the gas injection point and SOMEWHERE inbetween, you will likely have a flammable mixture.

ben

#9 César

César

    Brand New Member

  • Members
  • 4 posts

Posted 21 August 2006 - 02:29 PM

"Unregistered" i agree with you about the way how will take place the mixtura, so the fact is, i would have a flammable mixture. I agree with you that i have to see how much the tank breathes, and that´s why i decided not to connect the combustible gas to the vacuum breaker valve.

Proinwv, i understand your concern about the human response, and his intervention timely but this is not a normal condition, because this case will take place when the combustible gas supply fail (i should give reliability to this system) and the level of the tank (...of sour water) decrease fastly.

Thank you all for your comments, and your concern about this situation.

Greetings!

César