Flow Transmitter Upstream Or Downstream Of Control Valve?

flow transmitter control valve

This topic has been archived. This means that you cannot reply to this topic.
4 replies to this topic
Share this topic:
| More

#1 ezralh

ezralh

    Veteran Member

  • Members
  • 32 posts

Posted 23 February 2015 - 09:23 PM

Hi all good people,

 

At what condition that we put flow transmitter downstream of the control and what condition we put the flow transmitter upstream of the control valve. Thank you.

Attached Files



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,951 posts

Posted 23 February 2015 - 10:56 PM

ezralh,

 

System I in the attached file (flow element at upstream of the control valve) is always preferred, because in system II there is the risk of measuring error due to non smooth moving of the fluid at control valve downstream.



#3 breizh

breizh

    Gold Member

  • Admin
  • 6,332 posts

Posted 24 February 2015 - 01:00 AM

http://www.flowcontr...-considerations

 

Consider the link attached.

 

Hope this helps

 

Breizh



#4 SPC

SPC

    Junior Member

  • Members
  • 28 posts

Posted 24 February 2015 - 11:44 PM

Hi everyone,

 

        System -1 is always acceptable. As Fluid moves, flow tranmitter will measure & gives signal to accurately take an action for Control Valve. Hence, reading will be correct. There will not be time lag.

 

System-2 is unacceptable. As fluid moves, to take an action control valve has to wait till signal comes from its downstream side transmitter,

 

meanwhile some more flow would have passed through control valve. Here, there will be time lag. Hence, control function would not proper  response as per desired result.

 

Your comments are highly appreciated.

 

Regards,

SPC



#5 kiansafaie

kiansafaie

    Junior Member

  • Members
  • 23 posts

Posted 28 February 2015 - 11:18 AM

in addition of mentioned comment in some condition there is risk of two phase flow in down stream of control valve and the measuring of flow in this case is more complicated. Its better to have measuring flow at upstream of control valve.
Thank you