Please share with me what is best oxygen scavenger for following boilers:
1-pr :44 Barg
2-Temp. :274 centigrade
2-capasity :160 ton/hr
3-type of feed water :10% Dmw+90% return condensate
Best regards
M.RMRahimzadeh
|
Posted 16 April 2015 - 10:34 PM
Dears:
Please share with me what is best oxygen scavenger for following boilers:
1-pr :44 Barg
2-Temp. :274 centigrade
2-capasity :160 ton/hr
3-type of feed water :10% Dmw+90% return condensate
Best regards
M.RMRahimzadeh
Posted 17 April 2015 - 12:42 AM
Edited by breizh, 17 April 2015 - 12:51 AM.
Posted 17 April 2015 - 02:00 AM
Dear Breizh:
Due to some condition the known international mark not available,we currently use ammonium bi sulphite which causes our boiler PH reduce to danger acidic level.
Organic or inorganic which one you recommend?
REGARDS
M.R.Rahimzadeh
Posted 17 April 2015 - 02:25 AM
Posted 17 April 2015 - 02:48 AM
Mr Rahimzadeh,
Please check the dosing rate of ammonium bi sulphite; the relevant feed ratio (scavenger/dissolved O2, by weight) should be around 8 plus a margin
Hydrazine is no loger being used due to its carcinogenic effects in humans...
Posted 17 April 2015 - 02:57 AM
Dears :
I think the selection of Ammonium bi sulphite was wrong decision because it decompose at low temperature and lower PH of lower .
In addition i read in some text that ammonium bisulphite can be used in low temperature , for example waste water treatment and so on.
RAGARDS
Posted 17 April 2015 - 03:10 AM
Edited by breizh, 17 April 2015 - 06:31 AM.
Posted 17 April 2015 - 05:37 AM
I think the selection of Ammonium bi sulphite was wrong decision because it decompose at low temperature and lower PH of lower .
In addition i read in some text that ammonium bisulphite can be used in low temperature , for example waste water treatment and so on.
Mr Rahimzadeh,
Yes, ammonium bi sulphite is mostly used in low or moderate temperature applications such as water treatment systems. It normally begins to produce corossive gases at the temperature around 250 C and because the boiler you described is working at higher temperature i.e. 274 C, your judgment about the wrong selection of oxygen scavenger is appears to be right...
Posted 18 April 2015 - 05:34 AM
thank you so much
Cryogenic Distillation For Oxygen And NitrogenStarted by Guest_xyadap_* , 23 Mar 2023 |
|
|
||
Stripping Dissolved Oxygen From Water Using NitrogenStarted by Guest_MIZche_* , 06 Oct 2020 |
|
|
||
Determination Of Theoretical Oxygen DemandStarted by Guest_meer_* , 09 Feb 2020 |
|
|
||
Oxygen Line Depressurisation CalculationStarted by Guest_Ranga v_* , 09 Nov 2019 |
|
|
||
Oxygen Content Converted To Methanol ContentStarted by Guest_Phenom_* , 09 Apr 2019 |
|
|