#1 Broccoli Rob

Broccoli Rob

    Brand New Member

  • Members
  • 5 posts

Posted 27 May 2015 - 09:30 PM

Does anyone know of a credible resource that would provide guidelines for the number of air exchanges needed for a chemical storage building housing chlorine?



#2 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,727 posts

Posted 28 May 2015 - 02:49 AM

Check the following pages. Some of them refer to local and/or international standards:

 

http://www.iecfabche...ding_design.htm

https://www.acrp.com...nloads/cs_4.pdf

http://nepis.epa.gov...ekPage=x



#3 Broccoli Rob

Broccoli Rob

    Brand New Member

  • Members
  • 5 posts

Posted 28 May 2015 - 07:48 AM

Thank you very much for these links.  I have briefly looked through all of them and I believe they have what I need.  Thanks again.



#4 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,727 posts

Posted 30 May 2015 - 02:39 PM

The EPA document says that complete air change should be achieved within 1-4 minutes. I suppose this is the answer you were looking for.

Attached Files