Ro At The Sdv Flange

ro sdv condensate

This topic has been archived. This means that you cannot reply to this topic.
7 replies to this topic
Share this topic:
| More

#1 Mathi

Mathi

    Veteran Member

  • Members
  • 32 posts

Posted 04 July 2015 - 12:40 AM

I am working in a brownfield project. I came across the following arrange of RO after the SDV. I am not sure of its purpose but it was mentioned that the RO was sized for gas blow by case.

 

Since the SDV is after the level control valve, when low low level is reached the control valve is going to close any way. Therefore, there is no need to consider gas blow by case at all.

 

If anyone has any other ideas, please share.

Attached Files



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,952 posts

Posted 04 July 2015 - 04:21 AM

 

Since the SDV is after the level control valve, when low low level is reached the control valve is going to close any way. Therefore, there is no need to consider gas blow by case at all.

 

If anyone has any other ideas, please share.

 

Mathi,

 

There might be the possibility of LV open stuck or its relevant control loop malfunction leading to wide open position; then if the gas blow by case following to LV wide open is credible, putting RO at LV downstream can be a preventive facility...
 



#3 Mathi

Mathi

    Veteran Member

  • Members
  • 32 posts

Posted 04 July 2015 - 09:45 AM

Fallah

 

I am sorry. I failed to mention that the control valve is designed for Fail to Close (FC) condition.

 

So I don't think, we can consider the struck open condition but I am not sure whether a valve designed for Fail to Close case can reach struck open condition.



#4 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,952 posts

Posted 04 July 2015 - 10:35 AM   Best Answer

 

So I don't think, we can consider the struck open condition but I am not sure whether a valve designed for Fail to Close case can reach struck open condition.

 

Mathi,

 

Yes, it can reach stuck open condition or to be wide open due to relevant control loop malfunction; even if is being designed for FC condition...



#5 Mathi

Mathi

    Veteran Member

  • Members
  • 32 posts

Posted 04 July 2015 - 10:56 AM

Fallah

 

Okay. Thank you for very much for your responses. 



#6 breizh

breizh

    Gold Member

  • Admin
  • 6,340 posts

Posted 05 July 2015 - 02:41 AM

Mathi ,

What about the position of the shut down valve in case of lack of energy ( Air or power supply) ?

Just curious.

Breizh



#7 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,952 posts

Posted 05 July 2015 - 02:50 AM

Breizh,

 

A SDV or ESDV is to be designed in FC position....



#8 Mathi

Mathi

    Veteran Member

  • Members
  • 32 posts

Posted 05 July 2015 - 10:45 PM

Breizh

 

As Fallah said, the SDV is designed to Fail to Close.