Low Ph In Boilers Cbd


This topic has been archived. This means that you cannot reply to this topic.
7 replies to this topic
Share this topic:
| More

#1 mohsan

mohsan

    Brand New Member

  • Members
  • 4 posts

Posted 23 July 2015 - 09:40 PM

Hello Everyone

We are facing low pH (9.0~9.2) problem in our both boilers CBD samples since past month. We have one Auxiliary boiler operating at 50~70 ton/hr and one HRSG at 92ton/hr both producing steam at pressure of 39 Kg/cm2 (both boilers are water tube). Demineralized water is being used as fresh make up along with condensate return from Urea and DAP plants as boiler feed water after passing from tray type Deaerator. Amine treatment (ammonia solution) to control pH and Tri-sodium phosphate is being used as scale inhibiter. All other parameters remained normal along with pH of Demin. Water (7.0~7.5), condensate returns (10.1~10.2) and steam produced in boilers (10.1~10.2). There is not any leakage reported from process plants and all four types of condensate returns are none contaminated. Can anyone tell the possible cause and proposed solution of this problem? Thanks in advance.



#2 thorium90

thorium90

    Gold Member

  • Members
  • 1,073 posts

Posted 24 July 2015 - 07:38 AM

Is your make up rate still the same?



#3 breizh

breizh

    Gold Member

  • Admin
  • 6,347 posts

Posted 24 July 2015 - 08:45 PM

hi ,

To support your work.

Good luck

Breizh



#4 P.K.Rao

P.K.Rao

    Gold Member

  • Members
  • 265 posts

Posted 25 July 2015 - 09:53 PM

Please increase TSP dosage.



#5 mohsan

mohsan

    Brand New Member

  • Members
  • 4 posts

Posted 26 July 2015 - 06:02 AM

The make up rate is 30~40 m3/h higher but amine and TSP dosing rate also increased accordingly which maintained the pH of steam (10.1~10.2) and PO4 contents (~25ppm) in boilers CBD within the limits.  The main problem is low pH of boilers CBD.

Mr. P. K. Roy how much we can increase the TSP, we did it previously (about 35~40ppm) but no improvements observed. Is there is any signs of phosphate hide out in our system.



#6 thorium90

thorium90

    Gold Member

  • Members
  • 1,073 posts

Posted 26 July 2015 - 07:27 AM

Its possible then that the higher makeup rate could be causing the low pH. Try bringing your blowdown phosphate to about 35ppm with more TSP dosing. If the conductivity is still ok, you can increase ammonia dosage too.

 

Perhaps you might want to find out why the makeup rate is now higher. Was it sudden? Could there be a tube leak, or some passing valves?


Edited by thorium90, 26 July 2015 - 07:28 AM.


#7 P.K.Rao

P.K.Rao

    Gold Member

  • Members
  • 265 posts

Posted 26 July 2015 - 10:09 PM

Keep a check on sodium to phosphate mol ratio while increasing dosage of TSP. A value recommended by a few authors is 2.6 to 2.8..Excess of phosphate may cause phosphate hide-out. Keep a watch on boiler drum TDS. Please refer to ASME recommendations on TDS.



#8 breizh

breizh

    Gold Member

  • Admin
  • 6,347 posts

Posted 26 July 2015 - 11:13 PM

Hi ,

As per P.K Rao recommendations .

 

You may find assistance from the vendor of chemicals for your boiler . Tube leak ?

 

Hope this helps .

 

Breizh