Art,
I don't think that any overpressure device is necessary if there is no cause for overpressure. In the case of an air receiver, for example, if the air compressor discharge relieving device protects the vessel from that source, and there is nothing flammable to cause a fire, then no device is required. Process engineers have difficulty with this concept, and I have heard much discussion on the subject. I think the outcome of all the discussions would agree with you. And, no, it has not changed. A PSV was never mandatory.
For the service in question, if none of the input streams can overpressure the vessel, and there is no flammable nearby, then no overprotection device is required. If the nitrogen supply pressure can exceed the vessel design pressure, then protection is required. Likewise, if either of the liquid inlets can overpressure the vessel, this instance requires a PSV. And, of course, any reverse flow from the pump discharge that can overpressure the vessel must be evaluated.
The query was not well formed. Suggesting that Ankit needs some supervision in his organization to teach him how to conduct an analysis of relief requirements.
Bobby