Colt:
Your submitted graph supposedly showing the temperature drop in the storage tank doesn’t mean anything without reviewing the detailed calculations or source of the data. Without the ability to confirm that the presented data is valid and accurate, our Forum members can’t do anything else except acknowledge that it is your opinion or results and nothing more. Your reported partial tonnage of 275 tonnes of liquid Propane in the tank appears to be in error. My calculations, as shown in the attached workbook, show it to be 266.9 tonnes. Out of this liquid quantity you propose to consume 33.6 tonnes over a span of 4 days - approximately 12.6 %.
This may be, as you state, a very small amount of the stored propane that is extracted but it must be shown clearly that the remaining stored liquid propane temperature resulting from the internal vaporization does, in fact, not cause a low temperature problem. I have to explain all this because you don’t supply a flow diagram. And that is why I suggested an external evaporator that would vaporize the required 33.6 tonnes of liquid without lowering the tank’s temperature. My reason for suggesting this is that by vaporizing only the liquid required for gaseous fuel and sending this to the VDU unit, you keep the propane tank under normal conditions. Since you only require 350 kg/hr of propane, vaporizing this quantity should not be a problem. You could use an electric steam generator or even a hot water heated evaporator coil. I mention the hot water coil since you infer that your storage tank’s walls are enough to heat the tank and maintain a tolerable vapor pressure inside.
I doubt that you could expect to have the tank’s vapor contents heat up and maintain a tolerable vapor pressure using only the heat transfer from the ambient air. This is one of the most difficult heat transfer operations in industry because it involves surface heat transfer film coefficients on both sides of the metal wall that rely solely on gas films. Even if your outside air is strong enough to cause turbulence, you still have to contend with the fact that the vapor inside the tank is essentially static and has one of the poorest heat transfer coefficients to be found. All this means very poor and inefficient heat transfer over 60% of the sphere’s surface area. The remaining 40% of the sphere’s surface area is wetted with liquid propane and, although better than the vapor portion, is still a bad heat transfer condition because the contained liquid is static.
Your problem is one of unsteady state heat transfer. The tank’s contents are differentially cooling down due to the liquid content’s evaporation rate that is caused by the extraction of its saturated vapor content. This is the same effect that takes place in any mechanical refrigeration evaporation coil - except that your liquid refrigerant (the evaporating propane) is not being replenished but is, instead, a batch content of liquid that will differentially continue to cool down while its saturated vapor continues to be extracted. This is not a simple calculation and is going to involve some careful modeling of the operation in order to predict the resultant end temperature. That is why the detailed calculations are required for checking and review. A related flow diagram would be of value in following the assumptions and proposal.
Why are you proposing to employ an “RO”? I presume you mean a Resistance Orifice. I don’t understand the need for this because the orifice is not going to accomplish any control of the vapor extracted. That is the role of the proposed PCV (pressure control valve) - NOT A PRV - that is controlling the vapor pressure fed to the burner at the required 1.5 kg/cm2. The RO cannot do anything to control the drop in tank temperature. The rate at which the vapors are extracted is what affects the temperature of the liquid in the tank - and that rate is controlled by the PCV. Are you confusing a PCV with a Pressure Relief Valve? These are clear examples of why all engineers should always identify all acronyms employed. Again, if you supply a clear and detailed flow diagram of your proposed operation, these questions can be answered very quickly and accurately.
One safety instrument that I would install into a system that you are proposing is a pressure control on the required PCV feeding the VDU burner. The PCV should be fail closed and set to open only when the vapor pressure in the tank is above a set, safe value with respect to the safe saturated temperature. This would be a safeguard against drawing down the tank pressure lower than that pressure corresponding to the lowest acceptable saturated temperature.
If you have any follow up queries, comments, or statements on this topic then I highly recommend that you take the time and make the effort to submit detailed calculations and diagrams of the proposed operation. As Bobby Strain stated: “Proceed with deliberation”.