Temperature For Psv Selection As Per Api 526

psv relief temperature vessel design temperature

This topic has been archived. This means that you cannot reply to this topic.
5 replies to this topic
Share this topic:
| More

#1 Mrinmayee Marathe

Mrinmayee Marathe

    Brand New Member

  • Members
  • 3 posts

Posted 18 December 2015 - 04:34 AM

Dear All,

 

I have few Pressure Safey Valves, where for non-fire cases, the relieving temperature is lower than the design temperature of the equipment on which the PSV is mounted.

 

In such cases, while selecting the valve size as per API 526, which temperature shall be taken into consideration - the design temperature of the equipment or the relieving temperature?



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,949 posts

Posted 18 December 2015 - 06:29 AM

Hi,

 

The relieving temperature should be considered; because it's the coincident temperature of relieving pressure as design pressure of the relevant equipment...



#3 Mrinmayee Marathe

Mrinmayee Marathe

    Brand New Member

  • Members
  • 3 posts

Posted 18 December 2015 - 11:03 AM

Dear Sir,

 

Thank you so much for your reply. It is of great help to me.



#4 rajudhir01

rajudhir01

    Brand New Member

  • Members
  • 1 posts

Posted 11 January 2016 - 07:02 AM

I will go with the design temperature same as vessel.



#5 Ahsan67

Ahsan67

    Veteran Member

  • Members
  • 40 posts

Posted 04 November 2016 - 08:58 AM

Hi,

 

The relieving temperature should be considered; because it's the coincident temperature of relieving pressure as design pressure of the relevant equipment...

Dear Fallah,

 

Can you please guide me if it was a fire case and obviously relieving temperature will be higher than the operating for example in one of our case the vessel design temperature is 50C and the Fire relieving temperature is 128C  , should we still consider relieving temperature against the set pressure in API 526, it will be much helpful if you can provide reference for same.

 

Regards

Ahsan



#6 mirandomka

mirandomka

    Veteran Member

  • Members
  • 38 posts

Posted 04 November 2016 - 11:42 AM

Is the question regarding flange rating or design condition of the PSV inlet piping?

For design condition, I would suggest to check with your piping engineers and confirm if the short term exemption is whether or not applicable for your fire case.

For flange rating, you can follow the API 526 annex B to confirm based on your relieving temperature.

Edited by mirandomka, 04 November 2016 - 11:43 AM.