Fuel Gas Scrubber Bypass Piping Configuration

fuel gas scrubber bypass piping configuration isolation philosophy

This topic has been archived. This means that you cannot reply to this topic.
6 replies to this topic
Share this topic:
| More

#1 RUBABU

RUBABU

    Veteran Member

  • ChE Plus Subscriber
  • 30 posts

Posted 02 March 2016 - 04:19 AM

Wish to know about the recommended bypass piping configuration for a Fuel Gas Scrubber please. Choices are

1. bypass line with isolation valve

2. bypass line with isolation valve and spectacle blind upstream & downstream of isolation valve

3. bypass line with double isolation valve with one spectacle blind in between 



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,951 posts

Posted 02 March 2016 - 04:30 AM

RUBABU,

 

It depends on the maximum upstream pressure, the safety issue(s) of fuel leakage to downstream, bypass line main function,...



#3 RUBABU

RUBABU

    Veteran Member

  • ChE Plus Subscriber
  • 30 posts

Posted 02 March 2016 - 05:26 AM

a. Maximum upstream pressure is 180 psig.

b. no safety issue of FG leakage to downstream since downstream facilities consist of FG manifold for distributing FG to consumers. i.e. it is okay if bypass valve leaks (valve passing)

c. bypass line main function is to release the vessel for maintenance and to operate the vessel in bypass mode for a short period.



#4 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,951 posts

Posted 02 March 2016 - 06:03 AM

a. Maximum upstream pressure is 180 psig.

b. no safety issue of FG leakage to downstream since downstream facilities consist of FG manifold for distributing FG to consumers. i.e. it is okay if bypass valve leaks (valve passing)

c. bypass line main function is to release the vessel for maintenance and to operate the vessel in bypass mode for a short period.

 

RUBABU,

 

Then, I think a bypass line with an isolation valve and a spectacle blind at its downstream would be adequate...
 



#5 RUBABU

RUBABU

    Veteran Member

  • ChE Plus Subscriber
  • 30 posts

Posted 02 March 2016 - 11:11 PM

In that case the downstream spectacle blind would be used only for positive isolation of downstream section. i.e. the downstream section need to be shutdown to change position of spectacle blind from normal 'Blind Out' position to 'Blind In' position. right?



#6 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,951 posts

Posted 03 March 2016 - 12:06 AM   Best Answer

In that case the downstream spectacle blind would be used only for positive isolation of downstream section. i.e. the downstream section need to be shutdown to change position of spectacle blind from normal 'Blind Out' position to 'Blind In' position. right?

 

Yes, that's right...



#7 RUBABU

RUBABU

    Veteran Member

  • ChE Plus Subscriber
  • 30 posts

Posted 03 March 2016 - 12:23 AM

Thanks for the feedback Sir.