i have 2 trv in series for a line cooing from liquifaction ino the LNG storagae tank.
The line design pressure is 150psig. Athough it is a 2 phase line which i was worried about ,on the P&ID it is split into vapor and liquid lines.
so the line size is 2" and the following are the conds -
for 2 phase line
Press- 29 psia
temp- -243.6F
Comp-95%methane
1.44 % co2
95% methane
0.03% oxygen
vapor frac 0.0530
the line splits to liquid and vapor lines
both lines have 150 psig design pressure
I have got a this calc for liquid line as per API
SET PRESSURE 150 psig OVERPRESSURE 10% HEAT SOURCE solar radiation MAXIMUM HEAT EXCHANGER DUTY 3.30E+02 Btu/hr/ft2 DIAMETER OF PIPE 2 IN LENGTH OF PIPE 20 FT (assumed) SURFACE AREA OF PIPE 20.944 FT2 φ FOR SOLAR RADIATION (330 Btu/h-ft2 applied to surface area) SPECIFIC GRAVITY, d 0.43 CUBIC EXPANSION COEFFICIENT, αv 0.0009 1/°F MAXIMUM HEAT TRANSFER RATE, φ 1100.00 btu/hr SPECIFIC HEAT, c 1.115 Btu/lb F RELEIF RATE 0.004168 gpm VISCOSITY 1.066 cP
For gas phase i have used this calc
Q Length of pipe 10 assume Volume of the pipe 10.5 FT3 Pressure Max pressure of pipe 150 Psig 0.179 scfm 10.760
scfh
Q= ((V)*(MAEP/14.7)*(520/T1 - 520/T2))/60
Based on the following assumption
T1 = Degrees R, with 50 OF T2 = Degrees R, with 100 OF Based on worst case temperature rise from ambient heat gain based on 50 degree F rise in one hour
Please help me calculate the gas flow rate for the TRV i know it is 3/4"x1"
but my boss needs to know