Dear Sir
Sorry some of the datas are corrected here.We have amine regenerator column whose bottom temperature is maintained by two reboilers. The LP steam of around 4 Kg/ cm2(g) and capacity of 25000 Kg/hr (each reboiler) is used for heating purpose. The one rebolier condensate level is almost steady but the other level is always hunting. The condensate level pot is controlled by condendate level controller.LT was suspected faulty and it was replaced but it is still hunting. LG was cleaned and fluctuation is still seen on glass gauge.The level control valve does not fluctuate when taken on auto mode. The steam taping for fluctuating one reboiler takes from extreme header end and other one is also taking from header (around 7 m from extreme taping).The condensates of both level pots goes to deareator whose pressure is around 1 Kg/ cm2(g). The stalling effect is neutralised as we kept fully open the steam valve for both reboilers. Please suggest some ways to improve the condition of level pot.The condensate pot is around 6 m below the exchanger. The P& ID will be attached shortly.The taping of steam line means here the connection from header.
Edited by dhrubabasu2013, 15 April 2016 - 08:21 PM.