Here is my issue. We have right now vee-ball valves not globe. The original pressure drop specified in the vendor DS was just 5 psig for all three cases low flow/normal and max.
Off course I don't believe this so we manage to measure the drop with field data and found that we have more, around 20 psig, for the low case.
My problem is that from control point of view we need some DP on the valve but if we accept to much then reboiler will suffer since superheated steam is used instead of saturated.
If you use globe valve for small dp then you end up with a bigger valve size.
Bobby sorry but I don't understand your control mode. You need to change a variable in the equation Q=AU(Tc-Tb) in order to control so as the article posted by me describes that you can either change area, by the condensate level, or you change Tb by the steam pressure. You can also change pressure column, in theory, but this is not used normally.
To control level inside reboiler, the condensate pot has to have a right alignment with the tube bundle. In my case the pot level is much lower than tube level so we can't use this method. Even if we can't is not advisable for our case since we do super-fractionations and the response time will be very low. Also this method of control is harder to tune.
From my hysys calculation i found 3 psig drop with valve at 90%open and 7 psig drop with valve at 35% vor the max and min case.