Sour Water Pipe Line Thickness Loss


This topic has been archived. This means that you cannot reply to this topic.
6 replies to this topic
Share this topic:
| More

#1 Pronab

Pronab

    Gold Member

  • Members
  • 163 posts

Posted 20 May 2016 - 02:02 AM

One of the sour water filter PSV down steream(D/S) and it's by-pass line having severe corrosion. The pipe line has a nominal wall thickness of 5.54 mm and now it is measured only 1.1 mm (4.44 mm loss due to corrosion). Since the line is D/S of PSV and it's by-pass, the line is not used (used when PSV pop-up) and also since the D/S pipe line join with the inlet header, it is not easly repairable unless a total shut down. I want to know how to avoid this type of corrosion as a proactive measures for other pipe line. Even if we open by-pass line manually at regular interval what about PSV discharge line.

 

Thanks in advance.



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,930 posts

Posted 21 May 2016 - 03:21 AM

pronab,

 

Can you upload a simple sketch of the system you described...? It would be more helpful than the mentioned description in order to submit proper response to your query...



#3 Pronab

Pronab

    Gold Member

  • Members
  • 163 posts

Posted 21 May 2016 - 10:01 AM

Attached File  Sour water.pdf   1.03MB   27 downloads

 

 

This line is not used unless PSV pop-up. In the Filter-B, PSV D/S not found so much loss.

Sour water contains acid gas components mainly CO, H2S.


Edited by pronab, 21 May 2016 - 10:04 AM.


#4 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,930 posts

Posted 21 May 2016 - 12:36 PM

pronab,

 

When discharge of PSV on filter-B can be terminated to the atmosphere, why that of the filter-A cannot?



#5 CheAmine

CheAmine

    Junior Member

  • Members
  • 26 posts

Posted 27 May 2016 - 02:13 AM

Fallah,

I believe discharge of PSV located in filter B is also connected to the flare header. It seems like each filter is designed for 100 %, thats why each filter is having one PSV only.

Pronab,

Is there any possibility of PSV continuously passing leading to corrosion in the discharge piping ? In such sour conditions cant we put rupture disks upstream of these PSVs similar to Rich Amine flash drum PSVs ?!

Amine

#6 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,930 posts

Posted 27 May 2016 - 03:41 AM

Fallah,

I believe discharge of PSV located in filter B is also connected to the flare header. It seems like each filter is designed for 100 %, thats why each filter is having one PSV only.

Pronab,

Is there any possibility of PSV continuously passing leading to corrosion in the discharge piping ? In such sour conditions cant we put rupture disks upstream of these PSVs similar to Rich Amine flash drum PSVs ?!

Amine

 

Amine,

 

1-Please let the OP clarify about the termination of PSV discharge located on filter-B...

 

2-The severe corrosion per OP statement is at PSV downstream; then putting rupture disk at PSV upstream wouldn't remove the problem...
 



#7 Pronab

Pronab

    Gold Member

  • Members
  • 163 posts

Posted 27 May 2016 - 06:22 AM

Amine:

Both the filter PSV discharge is connected to the sour water I/L line of feed drum (As you can see in the drawing). I just mention one PSV(for A filter). Feed drum is connected to the Acid gas flare, should any acid gas flassh route to flare. However we didn't find any PSV pop-up or passing problem, It is become dead end. Accumulated sludges are found down stream of PSV. Agree with Fallah, additionally I don't think rupture disc is required here in low pressure service.

 

Regards.