Hi all,

 

     Currently, we have an improvement initiative to substitute the heating medium for an existing heat exchanger from Medium Pressure steam (15 barg) to Low pressure steam (7.5 barg). Obviously with lower pressure steam, the saturation temperature is lower too. Is there a way to calculate the time required for the different steam to heat the process fluid to the target temperature? I would like to know how much longer it takes for the low pressure steam to heat the process fluid.

 

 

Note: This is a continuous flowing process, not batch


Edited by Daniel James, 13 June 2016 - 10:51 PM.


#2 elstasso

elstasso

    Brand New Member

  • Members
  • 1 posts

Posted 01 July 2016 - 07:39 PM

everything you know about thermodynamics en heat/energy calculations but do it with mass flow instead of massand the flow will give you the time abscis



#3 latexman

latexman

    Gold Member

  • Admin
  • 1,687 posts

Posted 02 July 2016 - 04:37 AM

A P&ID and more details of the process description would help us help you.



#4 Daniel James

Daniel James

    Brand New Member

  • Members
  • 4 posts

Posted 26 July 2016 - 03:28 AM

A P&ID and more details of the process description would help us help you.

 

Please see this simplified drawing

 

schematics of E-6731.PNG

 

 

Currently, the heat exchanger is controlled by varying the level of condensate in the drum thereby changing the number of tubes exposed to the steam for condensing which changes the heating duty.

 

We want to substitute the 16 barg steam with 8barg lower pressure steam. My plant operator is concerned that it would take much longer to heat up the process fluid to operating temperature during startup.

 

From my understanding, as long as the current heat exchanger has sufficient surface area, it will consume the required amount of steam to bring the process fluid temperature to operating temperature. Am I wrong to assume that?



#5 latexman

latexman

    Gold Member

  • Admin
  • 1,687 posts

Posted 26 July 2016 - 07:12 AM

If the HX is too big (excess tubes flooded) with 16 barg steam and not too small with 8 barg steam, you are correct.  That's about a 30o C drop in approach.  Why would operations heat up the batch slower than the equipment is capable?  Is a different, parallel step the rate determining step?



#6 S.AHMAD

S.AHMAD

    Gold Member

  • ChE Plus Subscriber
  • 786 posts

Posted 30 July 2016 - 07:46 AM

Hi Dan

The LMTD will change. Let assume that the existing duty is Q1 that is:

Q1 = UA1LMTD1

The new duty  Q2 is given by:

Q2 = UA2LMTD2

 

U is about the same for the two cases.. Supposing that yo want to maintain the same time required then Q1 = Q2 that means you must adjust the condensate level such that it corresponds to surface area of:

A2 = A1.LMTD1/LMTD2 You can also determine the time by using the LMTD ratio.if you are maintaining the existing condensate level.

 

Hope the above short comments triggered your lateral  thinking. Good luck. 

 